akrub
21-10-2013, 12:42 PM
Hi All!
thermo king sl400e with controller thermoguard mp-VI errors 3 and 11.
There is broken wire to the sensor. I fix it but error is still active. :(
Can anybody tell me how to clear this error?

Thanks!

balathandapanis
21-10-2013, 01:31 PM
kindly check the signal continuty throughout the circuit.

IRMechanik
21-10-2013, 02:21 PM
try clearing the code through guarded access.

akrub
21-10-2013, 02:55 PM
all wiring from sensor are ok 100%
I have information about guarded access only for TG-VI but this different from µP-IV :(

gravy258
22-10-2013, 08:38 AM
power ON, cycles OFF, press TK button and CLEAR button at same time, before engine cranks.
This will take you to hourmeter screen. Clear alarms.
If no go to DDUR 45 press TK and CLEAR to guarded access menu. Clear alarms.

akrub
22-10-2013, 10:21 AM
error cleared Thanks!!! :)