02-03-2006, 11:17 PM
Is there a prefered percentage of run time for a condensing unit in a 24 hour period?

Ken

US Iceman
03-03-2006, 04:11 AM
The first question is related to method of defrost. If the system is medium temperature, then air defrost is probably used.

An air defrost cycle is longer than a positive defrost cycle such as electric or hot gas.

The total amount of time for the defrost periods is deducted from 24 hours. At design operating conditions, the balance of the 24 hours remaining (after deducting the defrost time) is what the capacity was probably based on.

fridg
03-03-2006, 05:56 AM
Depends on the system

minimum interval between two compressor starts
5 minutes

minimum compressor off time
2 minutes

minimum compressor on time
2 minutes

old gas bottle
03-03-2006, 08:04 AM
hi matey, lot of qoutes for equipement i get are based on 18 hr running time,hope this helps,cheers.

afeef
04-03-2006, 07:55 AM
Is there a prefered percentage of run time for a condensing unit in a 24 hour period?

Ken
hi sir
yes there is , it depends upon the outside temprature , as it varies up and down , the percentage of running also varies
the avarage of running is between 12 and 18 hour withen the 24 hour of the day
best wishes
afeef:D

Andy
04-03-2006, 09:38 AM
hi sir
yes there is , it depends upon the outside temprature , as it varies up and down , the percentage of running also varies
the avarage of running is between 12 and 18 hour withen the 24 hour of the day
best wishes
afeef:D

In the UK 18 hours would be the standard, but be careful of over sizing, if the unit is a bit on the large size, try selecting on a 20 hour run time, or where humidity is a problem use 22 hour run time.

Kind Regards. Andy:)