View Full Version : Ice formed on capillary tube



Desmond
02-03-2006, 11:44 AM
I'm wondering that ice formed on the outlet section (Just before evaporator inlet) of the capillary tube is normal. Anyone please comment on this situation.

Brian_UK
02-03-2006, 03:23 PM
No, not normal on an AC system although you can sometimes get frosting.

Abe
02-03-2006, 04:06 PM
I'm wondering that ice formed on the outlet section (Just before evaporator inlet) of the capillary tube is normal. Anyone please comment on this situation.


it means you short of gas

Desmond
07-03-2006, 09:20 AM
Other than short of gas, any others posibilities? The high side gauge is quite high as 305 psig for R404A.

stevo
07-03-2006, 07:35 PM
Other than short of gas, any others posibilities? The high side gauge is quite high as 305 psig for R404A.

could be liquid starved due to gas shortage/partially blocked drier/restrictor or compressor not fully pumping. what type of system ? :)

Desmond
08-03-2006, 02:05 AM
It's Chiller system. One condensing unit for two different refrigerated cabinets with different loads and temperatures.

chillin out
08-03-2006, 08:06 PM
Partial blockage in the drier?

Partial blockage in the cappilary?

Cappilary not sized properly?

Chillin:) :)