View Full Version : Carrier HAP - Air Flow rates



nevinjohn
08-10-2013, 01:31 PM
Hi,

For a heat load estimated with HAP, the fresh air requirment was 35lps, and HAP ouput shows that the supply air as 139L/s. Now my question is whether the AHU fan should be sized for 139L/s or the considering both fresh air and supply air, which is 35 + 139 Lps.
10808
Thanks
Nevin

moideen
10-10-2013, 05:20 AM
Hi,

For a heat load estimated with HAP, the fresh air requirment was 35lps, and HAP ouput shows that the supply air as 139L/s. Now my question is whether the AHU fan should be sized for 139L/s or the considering both fresh air and supply air, which is 35 + 139 Lps.
10808
Thanks
Nevin

Hello Nevinjohn

The Air System Sizing Summary reports the total supply fan airflow rate of 139 L/s which includes the 35L/s of Outdoor Ventilation Air.
Note the Supply Fan Sizing Data section lists the 139 L/s as the total supply air volume.
I trust this helps.

best regards
moideen-Dubai