View Full Version : Climaveneta Chiller



pavilion
28-09-2013, 08:23 AM
Hi All

CVM3000 Climaveneta chiller controller, need to calibrate the common evaporator outlet temp probe. I understand configuration setpoints 120 to 135 are temp probe offsets but need to know which probes these offsets refer to, any help appreciated.

Pavilion

install monkey
28-09-2013, 03:26 PM
http://www.mediafire.com/download/h3r19ghgcmx9iu3/CVM_3000.pdf
click on link for manual
have you got access passwords

pavilion
30-09-2013, 07:36 AM
Thanks Install monkey, I have this manual but the settings list does not identify the evap probes, have tried contacting Climaveneta but as usual no reply's :(. I have the passcode. Cheers.

goshen
01-10-2013, 08:01 AM
Hi
you need the wiring diagram !
st1 is probe 1 st2 is probe 2 all according to the wiring.
usually evap inlet us connected to terminals 5+6 and outlet to 7+8 on the board
all depending on model and no of circuits
good luck

pavilion
02-10-2013, 06:05 AM
Thanks Goshen, back on site next week will have a look then. Cheers.