View Full Version : Effect of Delta P of Evaporator on Mcquay Aircooled Screw chiller Compressor



ishtiaq ahmad
28-09-2013, 05:49 AM
We have Mcquay Aircooled Screw chiller McENERGY 143.2 Model HA-ST with MicroTech 11 C plus Contoller.The Designed Delta P of Evaporator is 4 psi.Would someone advise as to what would be the Effect on above Compressor,suction pressure& performance of chiller if Delta P ie the Difference b/w Evaporator inlet& outlet pressure is less than 4psi

Magoo
29-09-2013, 12:12 AM
generally would indicate low water flows through heat exchanger and would result in low suction pressures at compressor and the risk of freezing an evaporator tube.

MayankBhatia
21-10-2013, 06:10 PM
As Pressure drop directly proportional to water flow rate.So if pressure drop reduces water flow rate decreases.And delta T increases.As now water velocity is slow.and temperature reduces very fast and hence Suction pressure reduces.