View Full Version : Thermo King alarm code 77



frigoexpres
21-09-2013, 11:46 AM
Hi guys, please excuse my English.
I have a TK SMX2 with code 77-EPROM FAIL CHECKSUM TEST.
I want to reset the microprocessor to factory settings.
Please tell me how can I do a cold restart.
Thanks in advance.

frigoexpres
21-09-2013, 12:48 PM
P.S

Controller type is TGV I
ASSY P / N: 5D48192G35
BASE P / N: 5D48191G01

gravy258
22-09-2013, 03:22 AM
sounds like you need a new eprom(the microchip behind the four screw cover on back of door).
there not very expensive.
Cold start might give a temporary fix

frigoexpres
23-09-2013, 07:12 AM
Thanks for the reply gravy258. I will try with another chip.
However, I would like to try a cold start first time.
I would be so grateful if someone would tell me how
do a cold start.
Thanks in advance.

frigoexpres
23-09-2013, 02:17 PM
Ok. I see no one offers ...
First one who bothers to explain how to do
a cold restart, gets my installer for:
ReferManager, Data Manager and Report Program.

gravy258
25-09-2013, 07:53 AM
Relay Board Jumpers
The relay board jumpers are located just above
the largest connector at the bottom of the relay
board. They are arranged in four groups of three
pins each.

Go into guarded access write down sensor gradings and settings.

move jumper from TP5 to TP1.
switch on unit will be in cold start.
Switch off move jumper back to TP5 position.
Done.
Enter guarded access and re enter all values.

frigoexpres
25-09-2013, 07:22 PM
Hello gravy258. Please post an email address of where to send you the promised programs.
thank you

gravy258
26-09-2013, 09:23 AM
Hello gravy258. Please post an email address of where to send you the promised programs.
thank you

your OK mate, i've got all i need.