i got LG split air conditioner heatpump
i opened the indoor unit cover so i saw electric heater on the evaporator


http://im37.gulfup.com/op3T6.png

what its utility
for melting ice when evaporator frozen in cooling mode
or as backup heating when defros cycle energized in heating mode

The Viking
18-09-2013, 08:33 PM
You sure that is a heater and not an ionisation module?

:cool:

kefah
18-09-2013, 08:56 PM
im really not sure
but if we assume its electric heater
what its for

install monkey
18-09-2013, 09:18 PM
ioniser...
look at the nameplate for electrical load- prob around 50watt for fan motor and comms- if it was a heater then it would be of a higher output ;)

r.bartlett
18-09-2013, 09:21 PM
smoke removal

kefah
18-09-2013, 09:22 PM
ok
is there any wall amount heat pump contain electric heater in indoor unit or not

install monkey
18-09-2013, 09:28 PM
mitsubishi mr slims about 10yr ago used to have a boost heater option
imi hilo units had elec htr but theyre 20 yr old
any electric heater will affect energy efficiency ratings- also a fire hazard too- burgerkings used to use york ducted units with electric reheat batteries in the duct - lots of flashy lights when a 90kw 3ph heater bank blows an element

kefah
18-09-2013, 09:33 PM
mitsubishi mr slims about 10yr ago used to have a boost heater option
imi hilo units had elec htr but theyre 20 yr old
any electric heater will affect energy efficiency ratings- also a fire hazard too- burgerkings used to use york ducted units with electric reheat batteries in the duct - lots of flashy lights when a 90kw 3ph heater bank blows an element
ok
what is the utility of those heaters

for melting ice when evaporator frozen in cooling mode
or as backup heating when defros cycle energized in heating mode

install monkey
18-09-2013, 11:03 PM
on imi's they were for heating as reverse cycle heating in low ambients meant regular defrosting , on mitsi units they were an option to boost output -in cooling mode on any air con then the indoor shouldnt freeze up if aslong as the filters clean,setpoint is within limits and gas charge is ok

jdunc2301
19-09-2013, 09:35 PM
ok
is there any wall amount heat pump contain electric heater in indoor unit or not

Answered your own question

Steven Hsu
24-09-2013, 04:11 AM
It should be electric heater for winter use.