View Full Version : Neutral/Live connections, no indication anywhere? (Mitsubishi mini split)



gasmang
07-09-2013, 08:42 PM
Do Mitsubishi units not have specific requirements when wiring the outdoor unit with mains power for neutral and live connections? Checked through manuals etc, cannot find anything about N or L markings etc.

marc5180
07-09-2013, 08:47 PM
When you say specific requirements, do you mean which terminals they connect to?

gasmang
08-09-2013, 12:01 AM
Exactly, which terminals on the inside unit- they're not marked N or L etc, just some numbers

marc5180
08-09-2013, 08:12 AM
Exactly, which terminals on the inside unit- they're not marked N or L etc, just some numbers

If you are referring to Mitsubishi electric units, then normally the mains power (single phase or three phase) is fed from the distribution board to the outdoor condenser and connected to L1, L2, L3, N and Earth terminals that are marked.

From here a 4 core cable is normally run from indoor to outdoor S1 is live, S2 is neutral, S3 is comms and cable 4 goes to the earth terminal.

If you look at the wiring diagram on the indoor/outdoor pub you can normally work out which terminal goes where.

gasmang
09-09-2013, 12:41 AM
Thanks marc although in this case the outdoor unit is powered directly as this is a Heavy Industries unit.

marc5180
09-09-2013, 08:05 AM
Mitsubishi electric units are normally powered directly from the distribution board to the outdoor unit.

Do you have a model number?

Mitsubishi Heavy Ind normally work the same, mains power to the outdoor and 1 (Live), 2 (Neutral) and 3 (comms) interconnecting between indoor and outdoor.

Brian_UK
09-09-2013, 09:27 PM
As stated by Marc, check the wiring diagram on the unit covers.

install monkey
09-09-2013, 09:46 PM
some smaller units- under 5 kw are power to indoors and a 3 core and earth to the outdoor, some are power to indoor,power to outdoor and a 2 core signal between

Do Mitsubishi units not have specific requirements when wiring the outdoor unit with mains power for neutral and live connections? Checked through manuals etc, cannot find anything about N or L markings etc.

gasmang
10-09-2013, 03:38 PM
Thanks guys, the unit is a SRK-25ZJS.

Brian_UK
10-09-2013, 10:52 PM
According to the service/tech manual the wiring is :-
1. Live
2. Neutral
3. Signal

www.sun-ice.com.ua/docs/mitsubishi/scmzj-s_60_80.pdf (http://www.sun-ice.com.ua/docs/'mitsubishi/scmzj-s_60_80.pdf)