PDA

View Full Version : wont start



paralyz3rs
03-09-2013, 11:24 PM
Ok this is the situation. I have a SB3 sr whisper with a up6 micro. So my problem is that when I go to turn on the unit it just cranks and cranks. I found only 8volts on the high pressure cut out (so I tried bypassing that). Found that the 8dp wire for the hold circuit wasn't showing anything (bypassed that and got the unit to run). Took the bypass off I replaced a blown f6 fuse and now the fuel shut off pulls in then drops out and I get code 84 & 10

cadwaladr
04-09-2013, 12:56 AM
trace that wiring to the h/p you should have 12volts there,cut the incoming wires to the joint could be the problem,code 10 is h/p fault,dont run it too long bypassed!!!

sonkax
04-09-2013, 07:49 PM
if i remeber corectly that wire run through relay board, had the same problem once and the problem was on the back of the relay board.

gravy258
05-09-2013, 09:28 AM
Ok does it crank and crank immediately as you switch it on or does it go thru the routine first ?
If its the first, eprom failure.