View Full Version : Verifying TXV capacity



NiHaoMike
16-08-2013, 06:34 AM
I ordered a 1/4 ton R22 TXV (actually two) and it had a sensing bulb just a little smaller than a C battery. Thinking I might have got the wrong item or it was mislabeled, I decided to open it up to take a look at the actual valve assembly. To my surprise, the orifice was just big enough to stick a piece of AWG22 wire in it. Is that about right for a 1/4 ton R22 TXV? (There is an inscription on the valve that says 1/4, but I wonder if it was mislabeled. I would hate to carefully put together the system only to find out that the valve is completely wrong!)

mikeref
16-08-2013, 08:00 AM
What number is stamped on the orifice? 00 or 01?

NiHaoMike
16-08-2013, 02:16 PM
It's one of those:
http://www.ebay.com/itm/SPORLAN-IVE-1-4-GA-1-4-TON-TXV-EXTERNAL-EQUALIZED-47433-/220813007346

chemi-cool
16-08-2013, 05:13 PM
get a Danfoss TEX2 with orifice 00 and your'e done.

NiHaoMike
08-09-2013, 12:39 AM
As an update, I installed the valve and it worked great.