Hi guys.I have problem with a Clint liquid chiller(CRA/K 906-p) that uses Danfoss controller.After I switch on the unit, the controller starts the 6 hours delay.I cannot start the unit only after the 6 hours.Does anybody know how I can adjust this time shorter? It is a big problem because if there is a blackout in the summer there will not be cooling for 6 hours. Thanks for any ideas

chemi-cool
15-08-2013, 04:54 PM
Model of controller?

Soma
15-08-2013, 07:12 PM
MCX controller.It is all that I know about it.

chemi-cool
15-08-2013, 08:05 PM
http://www.danfoss.com/North_America/BusinessAreas/Refrigeration+and+Air+Conditioning/Literature/RA_Documentation.htm?CatalogKey=RA-6aa56192-f7e6-4793-b7f9-4c2fa908cc23-en-US:RA-6aa56192-f7e6-4793-b7f9-4c2fa908cc23-en-US&DocumentType=All&Language=en-US&FreeText=MCX&IncludeCurrent=True&IncludeArchived=False

Find your controller and change the required paraeter.

goshen
17-08-2013, 07:10 PM
Hi
as chemi stated this parameter ia accsesible via the local keypad!!