08-08-2013, 05:36 PM
Hi all
I've been called in on a private job to look at a Lenox package unit which some one has fitted in above a ceiling in a shop , it a huge thing hanging up on rod. Should be on a roof . But not there for that. It's got AL fault on control . I cnt find a thing about AL fault , dose any one know what it is .

install monkey
08-08-2013, 06:39 PM
if its a packaged unit- check the unit - if its an l box, theres a eng friendly pcb,if its a linea unit u need a kp02 controller to reset fault codes
what controller is it?

Paul a/c
08-08-2013, 07:18 PM
10627Yeah it's a package unit it's around 8 years old , I've got a pic of control not sure how to put it up from my phone on to here

jdunc2301
08-08-2013, 07:33 PM
Lennox controllers are always dirty!

install monkey
08-08-2013, 07:42 PM
http://www.lennoxemeia.com/product/terminals-fancoils/aria
cant find any manuals- but not much on it

Paul a/c
08-08-2013, 07:51 PM
Ok thanks il take a look .ive tryed powering system down but fault is up at once.

Paul a/c
09-08-2013, 07:05 AM
Hi all still can not find any fault for the AL fault I have which I have on control .all the faults I have found are all numbers. The system dose not run at all going to get a hove ceiling and have good look today . But any one know what this AL is ?
Thanks Paul a/c

leegally1983
09-08-2013, 01:17 PM
Hi all still can not find any fault for the AL fault I have which I have on control .all the faults I have found are all numbers. The system dose not run at all going to get a hove ceiling and have good look today . But any one know what this AL is ?
Thanks Paul a/c
Have you checked gas pressure?? I recall this fault code many years ago and the only faults I have had is LP and no control supply which was down to a transformer with a little trip switch on the side which had tripped down to a faulty solenoid on 4 way valve

Paul a/c
09-08-2013, 04:40 PM
Hi guy check above ceiling found covers off isolater has be break in on. Found 3 fuse out for main fan or condenser . Will pick up some new fuses test fan cables from contact to see if any thing is down to earth all ok there, someone has had a good play with it before .

Grizzly
09-08-2013, 05:05 PM
Hi Paul.
Have you any reference details for the package unit?
If it can be identified, I may be able to help further?
Grizzly

stufus
09-08-2013, 07:14 PM
For a start pull that Lennox bubble sticker off it , I'll be you a pound to a pinch of sh1t it say's Carel under it..
Usually...
AL alarm active it should give the actual code beneath
But depending on Lennox parameters could be generic code
Check the filters, probably icing up.
Cheers
Stu

Then again page 39
http://www.hvacrinfo.com/Controllers/carel%20aria.pdf

Grizzly
09-08-2013, 07:26 PM
For a start pull that Lennox bubble sticker off it , I'll be you a pound to a pinch of sh1t it say's Carel under it..
Usually...
AL alarm active it should give the actual code beneath
But depending on Lennox parameters could be generic code
Check the filters, probably icing up.
Cheers
Stu

Then again page 39
http://www.hvacrinfo.com/Controllers/carel%20aria.pdf

Beat me to it Stu.
I found this link.
But I suspect yours is better?
Steve.
http://www.carel.com/carelcom/web/eng/catalogo/gamma_dett.jsp?id_gamma=5

stufus
09-08-2013, 07:32 PM
We won't split hairs on this one Grizzly,
But knowing lennox it will probably be swings and roundabouts to reset the fooker.
Cheers pal
Stu

Paul a/c
09-08-2013, 08:01 PM
Thanks for help guys I am back there on Monday with new fuse il get a pic of the details and see what happens when I but new fuse in