I need some explanation regarding pressure and temperature of evaporation. I was working on a heat pump 60 kW refrigerant R407c, I've made some hydraulic reconstructions and charged it with completely with new refrigerant R407C - 16 kg.
The heat pump is working good but I measured the refrigerant pressure at the inlet of the evaporator and it was 7 bar which is about 14 C evaporation temperature but the outlet water is cooled to 7 C??? (condensation is about 22 bar). So the question is: does it happen some temperature glide inside the evaporator or is something else?

The Viking
31-07-2013, 08:13 PM
It would be easier to diagnose if you gave us all the data...

Temp of water in and out
Temp of refrigerant after the condensor and the evaporator

Would be a good start.


13-10-2013, 02:09 PM
Something's not right, 'cause the temperature of the refrigerant r407c is greater than the temperature at the outlet?