Hi guy has any come across P17 fault on a hitachi RAS-8FSG. Cnt find it in manual I have thanks
Paul

joe-ice
26-07-2013, 11:33 AM
Showing up in my book as inverter trip after 3 trips in 20 mins should throw up a code like 51 ,52 ,53.

The Viking
26-07-2013, 02:48 PM
Check the output from the inverter to the compressor, either with an inverter checker or a volt meter. With the compressor disconnected all three phases should be roughly the same when measured to neutral.

If the inverter is OK then check if the compressor is down to earth.

If all the above is OK you probably looking at a ciesed compressor.

:cool:

Paul a/c
26-07-2013, 07:32 PM
Thanks for the help you where spot on the invertor has failed test compressors both ok swapped over the invertor from anther unit which is not being used as floor is empty , all running great now , only need to find a hatichi supplier

install monkey
26-07-2013, 07:43 PM
climate ctr can get hitatchi stuff

Paul a/c
26-07-2013, 08:24 PM
Ok thanks il try climate control on monday