I was out at a thermoking TS200 today which is intermittently bringing up code 63 and when running takes forever to bring down the temp.

The sight glass is full
High side pressure 210 psi
low side pressure 30 psi
On defrost high pressure 300 psi

after about 45 mins of running the temp goes from 16c to 11c

slight chill in suction pipe

I have a feeling the defrost valve is leaking through but not 100% sure

on the unit there is no schreddar valve before the pressure regulator

Regards

Chris

djbe
23-07-2013, 10:39 PM
Hi All

I was out at a thermoking TS200 today which is intermittently bringing up code 63 and when running takes forever to bring down the temp.

The sight glass is full
High side pressure 210 psi
low side pressure 30 psi
On defrost high pressure 300 psi

after about 45 mins of running the temp goes from 16c to 11c

slight chill in suction pipe

I have a feeling the defrost valve is leaking through but not 100% sure

on the unit there is no schreddar valve before the pressure regulator

Regards

Chris

Hi Chris,
Discharge seems a bit low for these ambients?

Compressor problem?
Drop me a text tomorrow as a reminder as have check out procedure for TK scroll somewhere.

Take it easy.

Chris2005
03-08-2013, 03:27 PM
Hi Dave

Went back the next day to check the unit and it was working fine, and had no complaints since.

Thanks

Chris

djbe
04-08-2013, 12:59 AM
Hi Dave

Went back the next day to check the unit and it was working fine, and had no complaints since.

Thanks

Chris

Lucky!? Hope you are well mate? Pm me.