hi not a clue on heavy industries so any help gratefully received.SRC71ZE-S1, three indoor wall mounts showing run light always on and timer light flashing four times.PLEASE HELP ME

install monkey
03-07-2013, 08:46 PM
When a compressor discharge pipe sensor wire disconnection is
detected for 15 seconds or longer (less than 7ºC) after the outdoor
unit’s speed has continued at 0 rps or higher for 9 minutes.
(The air conditioner stops.)

install monkey
03-07-2013, 09:03 PM
Temperature (°C) Resistance (kΩ)
0 164
20 62
40 26

SeanMckenzie
04-07-2013, 06:49 AM
hi not a clue on heavy industries so any help gratefully received.SRC71ZE-S1, three indoor wall mounts showing run light always on and timer light flashing four times.PLEASE HELP ME

is your problem solved? i am facing similar issue so please help me out if you can..

europa
04-07-2013, 09:34 PM
not been back to the job yet,could be a while yet

install monkey
04-07-2013, 09:36 PM
if the sensor reads correct then check the gas charge

SeanMckenzie
05-07-2013, 06:28 AM
hi not a clue on heavy industries so any help gratefully received.SRC71ZE-S1, three indoor wall mounts showing run light always on and timer cheap hid headlight kits (http://www.robustbuy.com/lighting-system-hid-xenon-kits-c-492_645_653.html) flashing four times.PLEASE HELP ME

is your problem solved? i am facing similar issue so please help me out if you can..
Ok help me when you get it solved..

MagicMuppetMan
16-07-2013, 11:57 AM
This may be of help

http://www.mhiaa.com.au/PDF%20Upload/service%20support%20handbook/MHIAA_Service%20Support%20Handbook_07.13_v1.3.pdf

europa
17-07-2013, 10:00 PM
never went back.another company called in and no fault found ???

moondawn
20-07-2013, 12:24 AM
This may be of help

http://www.mhiaa.com.au/PDF%20Upload/service%20support%20handbook/MHIAA_Service%20Support%20Handbook_07.13_v1.3.pdf

Thanks for the manual mate