View Full Version : Panasonics CU-25R --What DCV at terminal of out door unit in normal operatioin ....



chanpn
23-06-2013, 06:01 AM
refered to ..

http://www.refrigeration-engineer.com/forums/showthread.php?36960-Panasonic-Inverter-CU-S10JKP-error-kode-H11-Help-me-any-body

My panasonics inverter air-con CU-25R show H11 error like that.

I've read the answer from that page and want to know more about the DCV. at terminal 2-3 on O/D unit at normal operation.

Many Thanks.

install monkey
23-06-2013, 12:33 PM
Is there any wiring error?
• Correct the indoor-outdoor units
connection wires
Check the indoor-outdoor units’ connection wires.
Disconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-70Vdc?
• Replace outdoor PCB
Reconnect terminal 3 wire and measure Vdc between terminal
2 & 3 from the outdoor unit.
Is the Vdc fluctuate between 20-50Vdc?
• Replace indoor unit PCB.

install monkey
23-06-2013, 12:38 PM
check your wiring isnt crossed between indoor/outdoor
check indoor fuse spur connections ok, and only switching 240v live and neutral- check wire 3 is thru crimped or terminal block- not switched or any external condensate pump hi pump alarm float isnt wired in

if unit still shows h11
then isolate outdoor unit, remove wire 3 (comms line)
test 2-3 should give a pulsating dc voltage upto 50vdc
if not check fuses,connection plugs on outdoor boards
i had a 48-50vdc signal on 1 and appeared to be indoor pcb, after swapping it- had to swap the outdoor pcb too

chanpn
27-06-2013, 09:05 AM
check your wiring isnt crossed between indoor/outdoor
check indoor fuse spur connections ok, and only switching 240v live and neutral- check wire 3 is thru crimped or terminal block- not switched or any external condensate pump hi pump alarm float isnt wired in

if unit still shows h11
then isolate outdoor unit, remove wire 3 (comms line)
test 2-3 should give a pulsating dc voltage upto 50vdc
if not check fuses,connection plugs on outdoor boards
i had a 48-50vdc signal on 1 and appeared to be indoor pcb, after swapping it- had to swap the outdoor pcb too