Got a daikin VRV r407c with E9 had daikin come and look and told us to replace EEVS replaced all EEVS and still the same fault. swapped boards over with another unit reset same fault?! what else is there to change?!
cheers
Paul a/c
18-06-2013, 06:31 PM
It could be the out door PCB at fault not sending the signal it monitors the voltage to the heads
AbsoluteWDJ
18-06-2013, 07:18 PM
Hey guys
Got a daikin VRV r407c with E9 had daikin come and look and told us to replace EEVS replaced all EEVS and still the same fault. swapped boards over with another unit reset same fault?! what else is there to change?!
cheers
Expansion valve cables, also have you cleared the fault on the local controls. press the test button once on each control 'E9' will display (last fault) then push and hold ON/OFF button for over five seconds
install monkey
18-06-2013, 08:11 PM
strainer gauzes-good luck
Deano240
19-06-2013, 10:00 AM
Weve swapped outdoor boards put new heads on put new cables? Even daikin are confused
Paul a/c
19-06-2013, 06:44 PM
That's a hard one to work out . If daikin don't know. then its going to be down to them to work it out . Could be a fault that no one has come across for before . Let us know what happens good luck
bratosin
19-06-2013, 08:04 PM
try to check gas senzor pipe and suction senzor pipe it`s posible one of them to be out of parameter.