Hi Gents,
I am quite new in this field and would like to request your kind advise.
I am in the Marine & Offshore HVAC field
I am now calculating one project by the following methods, Please correct me if i am wrong.
1) Calculating the supply air quantity by rooms' air change rate, to remove the sensible load ,fresh air requirement.
2) Calculating the cooling capacity by manually.
3) Cross checking by using ashrae psychrometric analysis CD version software.
The load is most likely the same in both calculation
*The problem is that sensible heat ratio that software provide and manul calculation is different in tons.And I cant put SHR line in chart according to my calculation. Let say on coil is 32'C @50%RH (32'C@50%RH), Off coil to be 11'C@8.1g/kg. SHR is 0.8. Software SHR is about 0.4
Kindly advise me in this issue