View Full Version : Service Manual of Midea Chiller
anil130
07-06-2013, 05:33 PM
Hi..friends
i need service manual for Midea chiller and below is the model number of it:
MGB-F65W/RN1
thanks in advance.
install monkey
07-06-2013, 08:42 PM
http://www.mediafire.com/download/yh4c9dc1hv99zeq/Midea_modularni_cilleri_MGB-service_manual.pdf
anil130
08-06-2013, 05:48 PM
@install monkey: many thanks for the info.. still i want to know that, is it possible if i make the chiller continuously running on cooling mood or is it possible to reduce the time up to 2 minutes after the completion of chilled.
install monkey
08-06-2013, 05:59 PM
maybe reduce the differential but typically u want 2 deg, also u still need a delay between starts- usually 3 mins, if you start compressors too frequently youll increase your electric bill and damage contactors,compressors- u might be able to lower ur setpoint but then u increase the risk of tripping on frost protection, maybe adding glycol (antifreeze) will allow a lower running temperature, dont know if theres an option to do this