BondingBilll
01-06-2013, 05:16 PM
I've fitted a new pcb board in Samsung AQV12VBCN and have tried a few different codes but it still isn't working - the outside compressor does not seem to work with any of the codes.
066064-170373
094777-17524E
084777-17521D
Does anyone know of any others that will work?
thanks for any help

install monkey
01-06-2013, 05:33 PM
Aqv12vbcn 0 5 4 7 7 7 1 7 5 2 1 d

install monkey
01-06-2013, 05:38 PM
http://www.mediafire.com/download/8b07mh8bq1p7u7l/AQV12VB_Vivace_Series_Service_Manual.pdf

BondingBilll
01-06-2013, 05:43 PM
Thanks, we have tried this number and still doesn't work, any other ideas?

install monkey
01-06-2013, 06:00 PM
http://www.mediafire.com/download/98e4b69vq59q4h2/adding_input_codes.pdf
check your doing the codes right, otherwise,a big hammer or a gallon of petrol;)

BondingBilll
02-06-2013, 12:50 AM
Thanks for the manual download i really appreciate it. Each time I press the mode button on the remote control unit it says on the display 00 00 00 press again says 1 0 00 00 and again says 2 0 00 00 and again 3 0 00 00. in the manual it says the default reading should be 1 or 0 how can i reset this. I think your right a Big Hammer & a gallon of petrol will be next :rolleyes: cheers Bill

install monkey
02-06-2013, 04:13 PM
http://www.samsungaccentre.com/php/home/downloadsLinks.php
last resort

BondingBilll
02-06-2013, 08:47 PM
Thanks very much for your help. I've been having problems with this for 12 months now. I phoned Samsung and they wanted £400 for a call out!
Thanks again

install monkey
02-06-2013, 08:52 PM
http://www.gallantairconditioning.com/technical-support.html
another samsung distributor

BondingBilll
02-06-2013, 10:00 PM
Cheers i will look into this. :) thanks again.
Bill

Loops
03-06-2013, 01:35 PM
Hi Bonding Bill,

Something I don't understand - you've fitted a board to the indoor unit (VBCN) to try to get the compressor to run in the outdoor unit (VBCX). Why?

The option code that Install Monkey gave you is correct.

Do you get any fault indication - LEDs indoor or outdoor flashing or error code somewhere?

Have you metered out to compressor windings? Checked to earth too? Do you get any current draw at all by the compressor? Have you tried an inverter checker on the inverter outputs?

Maybe - just maybe - it's an outdoor inverter board fault.

I think you must have spoken to a distributor because that price isn't correct for a Samsung engineer to come out.

Let us know what you've found so far so we have a chance of assisting.

Best Regards

Cheers

Loops

BondingBilll
03-06-2013, 10:14 PM
Hi Loops,
Thanks for the info I will get back to you tomorrow.
Cheers
Bill

BondingBilll
04-06-2013, 10:28 PM
Hi Loops,
I ran a few more tests with no luck. So decided to put the old PCB back in and test again. It all worked perfect with the new code but only when the PCB was 'hanging loose' outside the unit, as soon as I slotted it back into place it didn't work! I let the PCB 'hang loose' again and the machine was working for about an hour (heating & cooling, etc..). I switched the machine off and then back on again 10mins later to test again but now get an error code E472 which the manual says is 'AC Line Zero Cross Signal Out'. I'm at a loss what this actually means and what to do next. Any ideas?
thanks
Bill

install monkey
04-06-2013, 10:33 PM
any dry joints on pcb soldered pins?

BondingBilll
04-06-2013, 10:38 PM
Checked board no dry joints.

BondingBilll
04-06-2013, 10:46 PM
I will double check again for dry joints tomorrow just in case!
Thanks
Bill

install monkey
04-06-2013, 10:51 PM
maybe loose pins in the connectors- put the pcb in position and wiggle wires

BondingBilll
04-06-2013, 10:58 PM
Thanks install monkey,
will try.

Loops
17-06-2013, 02:56 PM
Sorry been bouncing around the country and not able get access to RE forum.

The error code indicates a loss of one of the power supplies onto the outdoor pcb, so I agree a dry joint or a dodgy connection through one of the multi pin connectors.

WITH THE POWER OFF try pulling each wire out of the connector to see if one comes loose. That'll be it.

Could be corrosion in one of the connectors so a bit of contact cleaner might be in order. Pull them all apart and rejoin a few times.

Let us know how you get on.

Cheers

Loops

VAGGOZ
05-12-2013, 03:00 PM
Thanks install monkey,
will try.
What happened eventually? 6 months still trying?