Grizzly
01-06-2013, 10:18 AM
welcome to the frum.Sheej.
Can you restrict yourself to a single post per item.
Multiple posts just clog up the system.
with the brief information you have given. I would guess you have either a unloader issue.
Where a cylinder/s unloaders are slowly unloading.
Or more likely you have a failed discharge non return valve.
Leaving the compressor subjected at start -up to discharge gas pressure.
Hence why the compressor rotates after sufficient time which has allowed the suction and discharge pressures to equalise.
Grizzly
Can you restrict yourself to a single post per item.
Multiple posts just clog up the system.
with the brief information you have given. I would guess you have either a unloader issue.
Where a cylinder/s unloaders are slowly unloading.
Or more likely you have a failed discharge non return valve.
Leaving the compressor subjected at start -up to discharge gas pressure.
Hence why the compressor rotates after sufficient time which has allowed the suction and discharge pressures to equalise.
Grizzly