Very simple super heat & sub cooling question for you all if that's ok? Just to make sure I'm right
The scenario first R407c refrigerant on a basic air/water chiller with small plate heat exchanger.
Ambient air today 11 degrees.
Super Heat - Suction gauge line connected to the Schrader connection just before the screw compressor. Pressure 3 bar (converted I make that -4 degrees)
My Fluke thermometer is reading a suction line pipe temperature of 9.5 degrees (its not an infrared, K couple)
Sum = 9.5 - -4 is 13.5 degrees of super heat.
Sub Cooling - High side gauge line connected to the Schrader connection just before the expansion valve after the liquid inline core drier. Pressure 16 bar (converted I make that 40 degrees)
thermometer is reading a liquid line pipe temperature of 26 degrees (measured just before where my line is connected)
Sum = 40 - 26 is 14 degrees of sub cooling.
Seems to me I have high sub cooling and low super heat?
R407c refrigerant charge has been charged to data plate (72kg) so can't be low on charge, can it?
Hope this makes sense, is this the correct way to work out the equation?
thanks
The scenario first R407c refrigerant on a basic air/water chiller with small plate heat exchanger.
Ambient air today 11 degrees.
Super Heat - Suction gauge line connected to the Schrader connection just before the screw compressor. Pressure 3 bar (converted I make that -4 degrees)
My Fluke thermometer is reading a suction line pipe temperature of 9.5 degrees (its not an infrared, K couple)
Sum = 9.5 - -4 is 13.5 degrees of super heat.
Sub Cooling - High side gauge line connected to the Schrader connection just before the expansion valve after the liquid inline core drier. Pressure 16 bar (converted I make that 40 degrees)
thermometer is reading a liquid line pipe temperature of 26 degrees (measured just before where my line is connected)
Sum = 40 - 26 is 14 degrees of sub cooling.
Seems to me I have high sub cooling and low super heat?
R407c refrigerant charge has been charged to data plate (72kg) so can't be low on charge, can it?
Hope this makes sense, is this the correct way to work out the equation?