kengineering
07-02-2006, 02:15 AM
I didn't see an arrow or the word TOP on it so I figure it doesn't mater. What say you?
Ken

frank
07-02-2006, 04:16 PM
Well, I did a quick search on Google and most of them said " multiple mounting positions" then I found this - so now I'm not sure http://relays.tycoelectronics.com/datasheets/38_Series.pdf

Refer Rick
07-02-2006, 09:05 PM
Yes, potential relays are position sensitive. Each must be calibrated for the position it's to be used in. By installing one in an incorrect position, you risk, altering the Pick up and Drop out voltages.
Rick

vEStMaN
07-02-2006, 09:34 PM
Hi,
P.relays usually sit in the upright position they are gravity assisted to switch over from start to run,lying them down (connections at the top) inhibits the cross over, causes the relay to stay in start position thus burning out the start windings.

guy in blue van
08-02-2006, 12:47 AM
depends on make of relay
for instance copeland oem relay is position sensitive but an aftermarket such as mars is multi positional

guy in blue van
08-02-2006, 01:01 AM
usually the cheaper relays are position sensetive which is the reason compressor manufactures love them

kengineering
08-02-2006, 01:09 AM
This partiular relay came with a Danfoss factional hp. ( no markings) with a start cap and run cap.
Ken

wambat
08-02-2006, 01:29 AM
I didn't see an arrow or the word TOP on it so I figure it doesn't mater. What say you?
Ken
IT's position sensitive and normally closed:)

Dan
08-02-2006, 01:59 AM
I didn't know potential relays sensitive to position. Dang, all these years. Seems most are mounted spade up, but I recall hundreds mounted on the back wall and at other tilts.

guy in blue van
08-02-2006, 04:25 AM
if it came with replacement comp than play it safe and mount it the way the old one is mounted

kengineering
08-02-2006, 11:04 AM
if it came with replacement comp than play it safe and mount it the way the old one is mounted

The old compressor only had a start cap w a cmr relay. The replacement has both a start and run cap with a potential all supplied by Danfoss. No mounting bracket or instructions will have to make something.

Ken

guy in blue van
10-02-2006, 01:09 AM
give me some numbers Ill look it up if you havent already isntalled it or blew it up.:)