View Full Version : what are these accessories in split ac outdoor unit
kefah
20-05-2013, 10:26 PM
hi
today i repaired an ac split unit
acc 24000 BTU
but i found 2 accessories in the outdoor unit between the discharge valve and condenser
10368
i think the one in the left is filter
but im not sure
so
what are these accessories and their utility
Brian_UK
20-05-2013, 10:45 PM
Yes the one on the left looks like a filter and the right hand one is simply a collector for the condenser liquid discharge where it then goes through the two expansion capillaries.
install monkey
21-05-2013, 07:49 PM
10370
normally a peice of enlarged pipe with 2 grooves around it indicates a strainer- bit of gauze- see the restriction inside
kefah
21-05-2013, 08:30 PM
thank u
i removed them today and checked them
both contain filter screen
kefah
23-05-2013, 09:11 PM
so
the filter in the right is for preventing the blockage of capillary tube
but what is the utility of left filter ??????
its for preventing the blockage of indoor unit ???
or prevent the blockage of capillary tube in reversed cycle (heating mode) heat pump ??????
Brian_UK
23-05-2013, 10:55 PM
All of the above.
Josip
23-05-2013, 11:14 PM
Hi, kefah :)
so
the filter in the right is for preventing the blockage of capillary tube
but what is the utility of left filter ??????
its for preventing the blockage of indoor unit ???
or prevent the blockage of capillary tube in reversed cycle (heating mode) heat pump ??????
seems you know the right answer .... when we have bidirectional refrigerant flow it is good to have capillary protection on both sides ....
Best regards, Josip :)
kefah
25-09-2013, 08:26 PM
thank u all
Powered by vBulletin® Version 4.2.1 Copyright © 2024 vBulletin Solutions, Inc. All rights reserved.