PDA

View Full Version : mitsi electric 6608?



Pugwash
20-05-2013, 08:43 PM
hi all.

working on few pury systems linked back to g50 then onto sites local network/laptop etc.
g50 showing fault at cond 051 with 6608, noise on mnet. been running for 4 year without fault, all cables screened and correct size, earthed correctly..

any ideas??

thanks

Brian_UK
20-05-2013, 10:49 PM
Have you checked the voltage on the comma lines?

Pugwash
21-05-2013, 07:14 PM
yep 29vdc on mnet

Neddy
21-05-2013, 07:15 PM
Had the same error last week. Turned out I was missing voltage at L3 due to a poor connection in the isolator. Did a full system reset and it cleared the fault.

install monkey
21-05-2013, 07:42 PM
had it on a hotel- system 4yr old and the comms goes through the power pack before the g50- power pack failing ,thus the comms error

Pugwash
21-05-2013, 10:59 PM
appreciated, off site this week now but will check out mains / power pack etc when back.

AbsoluteWDJ
27-05-2013, 09:46 PM
hi all.

working on few pury systems linked back to g50 then onto sites local network/laptop etc.
g50 showing fault at cond 051 with 6608, noise on mnet. been running for 4 year without fault, all cables screened and correct size, earthed correctly..

any ideas??

thanks
How long is the total cabling?
Do you have a booster installed?

stufus
28-05-2013, 10:42 AM
Check the position of the cn41 plugs on the outdoor board.
Cheers
Stu