What symptoms will occur if the (IPR) is parttially open? Would I have lower than other than normal suction and superheat at the evap .
bwd111
16-05-2013, 01:12 AM
Would I have higher current draw as well
Peter_1
17-05-2013, 02:09 PM
HP and LP will be almost the same, compressor body will be extremely hot and AMPs will be lower.
sendhilkmar
20-05-2013, 12:26 PM
At the time of IPRV opening , you can hear the audible noise. The suction and discharge pressure equalizes rapidly
Regards,
Sendhil