View Full Version : Help with TXV selection



kengineering
29-04-2013, 08:34 PM
Customer requesting a txv for 50*f liquid. Its a somewhat clouded message because in another email they asked for a 50*f subcooled valve. Can anyone shed some light for me here or do I need more info from them.. As always, thanks guys.. Kengineering

chemi-cool
29-04-2013, 08:51 PM
to choose the right TXV you will need more info than what you have such as: type of refrigerant, evaporating capacity, cooling capacity, room temp, pressure drop,

Every TXV catalog will give you the right info.

sendhilkmar
09-05-2013, 11:45 AM
Hi,</SPAN></SPAN>
Refer the attached Danfoss catalogue page which explains the selection procedure of TXV. </SPAN></SPAN>

Regards,</SPAN></SPAN>
Sendhil </SPAN></SPAN>