View Full Version : Alarm 38 on unit THERMO KING UTS 400



incar
23-04-2013, 01:31 PM
Hello, I have a problem with ALARM 38 on THERMO KING UTS 400.... can we help me, please?? Thanks

jazzhands
23-04-2013, 09:39 PM
Electric phase reversed? That's what's on my tk alarm list anyway.

incar
23-04-2013, 09:49 PM
Electric phase reversed? That's what's on my tk alarm list anyway.
Thanks for reply, Is it possible to bypass it??

jazzhands
23-04-2013, 09:56 PM
Honestly not sure if u can bypass it. Im Sure someone on here will be able to answer that.

incar
23-04-2013, 10:16 PM
I hope....

jazzhands
23-04-2013, 10:41 PM
http://www.xtralease.com/SiteCollectionDocuments/Reference%20Guides/Thermo%20King%20Alarm%20Codes.pdf

cadwaladr
24-04-2013, 12:00 AM
change two of the phases around on the incoming plug/swap two wires around on incoming.

incar
24-04-2013, 01:33 PM
change two of the phases around on the incoming plug/swap two wires around on incoming. I have already changed the two phases but always appears the alarm... and now???

cadwaladr
24-04-2013, 06:58 PM
guess its the module that sense,s the incoming power,it should be strapped to the incoming at the contactor,disconnect the three wires and see what happens DONT FORGET TO DISCONNECT THE POWER SUPPLY FIRST!

incar
24-04-2013, 07:54 PM
guess its the module that sense,s the incoming power,it should be strapped to the incoming at the contactor,disconnect the three wires and see what happens DONT FORGET TO DISCONNECT THE POWER SUPPLY FIRST!When I disconnect the three fase on module, the unit run on diesel mode... Is it possible to bypass the module??*

Mick Carroll
24-04-2013, 09:03 PM
Check to make sure you have correct voltage at the contactor, Not possible to bypass the module.

incar
24-04-2013, 09:46 PM
Check to make sure you have correct voltage at the contactor, Not possible to bypass the module.
At contactor (wherethe 3 phases arrive in first time) I have the correct voltage

gravy258
25-04-2013, 02:09 AM
i'd be sure its the auto phase reversal module on the relay board, the black box looking thing in the top RH corner.
TK SR units all have this.

incar
25-04-2013, 10:04 PM
i'd be sure its the auto phase reversal module on the relay board, the black box looking thing in the top RH corner.
TK SR units all have this. I know it and I wanna know if it is possible to bypass the module... I dont want change it

IRMechanik
26-04-2013, 06:45 PM
I know it and I wanna know if it is possible to bypass the module... I dont want change it

as stated, not possible to bypass the module.
Early revision interface boards had the module integrated into the board (grey cover)
Later revision boards have it as separate module (black box)

incar
26-04-2013, 06:56 PM
how can I be sure that the alarm 38 is caused by this module?How much it cost??

IRMechanik
28-04-2013, 12:49 PM
how can I be sure that the alarm 38 is caused by this module?How much it cost??

Based on what you've told us and the armchair diagnostics of several experienced techs, it sounds like the module. As I tell people over the phone, hold it up to the phone and I'll tell you what's wrong.

the only way to confirm the diagnosis is to plug a new module in. Unfortunately the second you plug in an electrical component, you own it.

Unless you can find someone with a good used one you can try, your options are pretty limited.