Please give me some suggestion how to calculate the PDU and KW for the following coldroom.

Room Dimension: 3615mmX3615mmX4038mm(H)X75mm(T)
Temperature Require: -2'C
Storage: Chinese Broccoli/Kai Lan
Frequency To Open Sliding Door: 20% per Day.

How To Calculate The PDU and KW For this coldroom without any support of software.
Please Advice The Calculation.
Thanks a lot...

smpsmp45
23-04-2013, 07:09 AM
I think the product incoming temperature & its quantity is also needed here.

If you Send your email, I can send you basic calculations

hongyunref
23-04-2013, 07:18 AM
I think the product incoming temperature & its quantity is also needed here.

If you Send your email, I can send you basic calculations

Thanks For Your Reply, Really Appreciate.
Kindly Send the calculation to this email add: hongyunref@hotmail.com

lh.ahn84
17-06-2013, 01:09 AM
You will need to calculate the transmission load. Then add in the pull down load.

HVACRAU
18-06-2013, 07:35 AM
In Australia, if not too much pull down load, just make it 265W/m2 will do.
And you can go 240W/m2 if you want.

HVACRAU
18-06-2013, 07:40 AM
If not too much pull down load, just make it 265W/m2 will do.
And you can go 240W/m2 if you want.