17-04-2013, 06:10 AM
Hi All,
I'm new to learn and gain knowledge in this industry and currently facing a problem regarding the calculation part for refrigerant's superheat and sub cooling,
I searched few ways to calculate but answers that I get is different.
As other website suggested, I get these information to calculate superheat and sub cooling:
Suction Line Temperature: 4'C/39.2'F
Suction Line Pressure: 32psi / 17.30psig
Liquid Line Temperature: 41.5'C/106.7'F
Liquid Line Pressure: 230psi / 215.30psig
Indoor Temperature: 3.5'C/38.3'F
Outdoor Temperature: 27'C/80.6'F
Additionally, is superheat and sub cooling can indicate us the way to control humidity (RH%) in the cleanroom? Because current RH in cleanroom is excess that the RH required.
Thanks...