View Full Version : Carrier 30 XA high pressure



Palkoper
12-04-2013, 04:34 PM
Hi Guys just want make sure if I am right with High Pressure diagnose on CARRIER 30 XA water chiller . So all fans are Ok ambient temperature is 10 degrees and after 5 - 6 hours chiller stop working cos of HP . All condenser and fans are OK but I found small leak on pressure relief valve see picture ...


It could be problem with refrigeration or not really ....

BTW chiller when is starting is so NOISY with hissing noise .



Thanks 4 any advice


Cheers

Arshid Siddiqui
30-05-2013, 06:07 PM
please reset the high pressure switch mounted on compressor high pressure line.

install monkey
30-05-2013, 09:11 PM
http://www.mediafire.com/view/2r3b6pdqi2b7ul5/30xa-4t.pdf:)

goshen
03-06-2013, 10:46 AM
Hi
check your hp sensor , this could leed to problems as you discribe , expecially if unit works well for 5 hours!
good luck

serviceman
04-06-2013, 07:35 PM
the machine has electric valves on the discharge?