11-04-2013, 05:12 PM
I have a city multi p125 and 2 indoors p63s with one par 31 remote .the remote cable was never looped in ,can I change settings with a par 27 remote to get both units to run and then take off par 27 back off system if so how or will I just need to run a new cable
cheers

Neddy
11-04-2013, 05:31 PM
You need to run a new cable if you want to use the PAR 30.

JoeAT50A
12-04-2013, 07:10 AM
Unfortunately when there is no centralized controller or system controller, ME an MA remote controller can not be used together in a system. Bet is to use all either ME or MA. Of course you need to run a loop (TB15) cable for grouping with MA. ME plus point is that you need not to run extra cable for such situation.

ballvalve
13-04-2013, 11:07 PM
Cheers joe . Just going to run a loop in . Had just heard that if I hook a par 27 up to one of the indoors I could tell it it has the same remote address and take the par 27 back off so I wouldn't have to run the loop.