goldpau
20-03-2013, 06:27 PM
Hi all,
Had a general look through on past posts and some people recommend insulating both refrigerant lines whilst others say you only need to insulate the suction line and not the liquid line - we have always insulated both as its Ac and thats what I was taught.
Going to be replacing some R22 systems next month with new R410a cool & heat systems and aim to re-use pipework (its the correct size), suction lines are all insulated but none of the liquid lines are insulated, was just going to insulate them but for 4 of the systems the pipework runs through an area which we cant get to (one section is above plasterboarded ceiling & another section is under the floor) & main builder doesnt want us doing 'too much damage'.
So I know that by not insulating this section of liquid line there will be a slight reduction in performance (not really a big deal as system is slightly oversized anyway as calcs show it needs 6.2kw and we are installing 7.1kw systems) but will we have any other problems?
One of our guys mentioned the liquid line will sweat (condensation) when the system is used in cooling mode and this will damage the plasterboard ceiling & thats why it needs insulating but one of our other guys said no it wont the old system was a cooling system and the liquid line wasnt insulated and didnt sweat and looking at the ceiling theres no damage so he has a point.
Any other thoughts? Are we just looking at a slight drop in efficiency thus performance or will we get a condensation problem? (struggling to see how we would get a condensation problem as the old systems havent had a condensation problem but Im open to others thoughts)
Cheers
Had a general look through on past posts and some people recommend insulating both refrigerant lines whilst others say you only need to insulate the suction line and not the liquid line - we have always insulated both as its Ac and thats what I was taught.
Going to be replacing some R22 systems next month with new R410a cool & heat systems and aim to re-use pipework (its the correct size), suction lines are all insulated but none of the liquid lines are insulated, was just going to insulate them but for 4 of the systems the pipework runs through an area which we cant get to (one section is above plasterboarded ceiling & another section is under the floor) & main builder doesnt want us doing 'too much damage'.
So I know that by not insulating this section of liquid line there will be a slight reduction in performance (not really a big deal as system is slightly oversized anyway as calcs show it needs 6.2kw and we are installing 7.1kw systems) but will we have any other problems?
One of our guys mentioned the liquid line will sweat (condensation) when the system is used in cooling mode and this will damage the plasterboard ceiling & thats why it needs insulating but one of our other guys said no it wont the old system was a cooling system and the liquid line wasnt insulated and didnt sweat and looking at the ceiling theres no damage so he has a point.
Any other thoughts? Are we just looking at a slight drop in efficiency thus performance or will we get a condensation problem? (struggling to see how we would get a condensation problem as the old systems havent had a condensation problem but Im open to others thoughts)
Cheers