could someone point me in the right direction, regarding evaporator defrosting, mainly the fin spacing and effect on the defrost.
correct me if im wrong
the smaller the fin spacing, equals the more fins per inch, resulting in a greater surface area, and making frost build up easier due to the smaller gaps between the fins.
as a result the defrost period would have to be increased and the interval more often, the the same size evap with a bigger fin spacing and less fins per inch

install monkey
04-03-2013, 09:42 PM
fridge or freezer??

james10
04-03-2013, 09:51 PM
Both........

install monkey
04-03-2013, 09:54 PM
any fridge should have off cycle defrost by either 3 deg deadband on the stat to defrost an evap or if fanned then again- anything over a 2 deg diff would be sufficient, sometimes a 4x20 min defrosts with just fan will cure it, for a freezer at -18 then again 4 defrosts for upto 40 mins with electric defrosts with a termination stat setpoint of 25deg and a 2 min fan delay or 2 min dripping time

james10
04-03-2013, 10:01 PM
That's true, but what considerations should be made with different fin spacing with regards to defrosting

install monkey
04-03-2013, 10:06 PM
you havent given us much details into the application, do you want a manual???:D

james10
04-03-2013, 10:11 PM
This is just a generalisation, regrading fun spacing and defrost, I'm good for manuals ;)

install monkey
04-03-2013, 10:17 PM
http://uk.grundfos.com/service-support/encyclopedia-search/fin-spacing.html

install monkey
04-03-2013, 10:18 PM
http://books.google.co.uk/books?id=n5-9_WnXhWMC&pg=PA27&lpg=PA27&dq=evaporator+fin+spacing&source=bl&ots=ovJnaSRVxZ&sig=9Z4-Iyh4KWO69xmeQQcwZnikODA&hl=en&sa=X&ei=SB01UZ_JLumX0QX0sYCIDg&ved=0CFAQ6AEwAw#v=onepage&q=evaporator%20fin%20spacing&f=false

james10
04-03-2013, 10:26 PM
gotta share the love :)

Iceman717
05-03-2013, 04:50 PM
Tighter fin spacing is going to make defrost more frequent because you'll obstruct airflow faster. Depending on the defrost method, defrost duration could be shorter.

MikeHolm
06-03-2013, 11:49 AM
My local mentor designs his coils with 10-12fpi, more packed than that wastes defrost energy but I can see why the japanese pack them in, way less manufacturing/shipping costs