PDA

View Full Version : Samsung DVM series problem.



HARRY 7
26-02-2013, 07:32 PM
Hello to everyone.I have alarm Eo to the above model.Can anybody help?The alarm appears to both indoor units.

Brian_UK
26-02-2013, 08:55 PM
Sorry, don't recognise the E0 code, try this download for error codes...
http://www.logicool-ac.com/samsung_technicaldownloads/DVM%20Fault%20Codes%20and%20Diagnosis.pdf

HARRY 7
27-02-2013, 01:05 AM
Thanks for reply Mike.I have this manual.I cannot find anything.The outdoor unit is with R22.

RusBuka
27-02-2013, 05:17 AM
Malfunction in the outdoor block:
• Temperature or pressure sensor is faulty.
• EEV (after 6 - го mistake detection) is faulty.
• Wrong alternation of power phases or lack of a phase.
• Disruption of communication with the outdoor block.

HARRY 7
27-02-2013, 06:38 AM
Thanks for the help RusBuka.Do you have the troubleshooting of that alarm?I also have an indoor four way cassete where the five leds (filter-fan-on,off-timer-defrost)flashing.The manual says Eeprom option error.What is the meaning of this alarm?

RusBuka
27-02-2013, 03:29 PM
This mistake arises on the wire MCM-A100 panel which allows to operate functionality and is connected to the central panel. Unfortunately at me manual only in Russian.

Concerning EEPROM and the indoor block, write its model.

RusBuka
27-02-2013, 03:37 PM
Mmmm, find what you need)))

http://yadi.sk/d/wwcEmzBf2w-vQ

HARRY 7
27-02-2013, 05:30 PM
Indoor cassete model AVMCH070.

RusBuka
28-02-2013, 02:42 PM
Try to enter an option code from the wireless panel
04 52 00 1C 00 00
If not in a course as to do it, read a manual. It if the code flied. I precisely don't remember, whether it is possible to register with s-net without the panel.
http://www.kvent.com/litterature/SAMSUNG/dvm-manual.pdf

HARRY 7
28-02-2013, 09:31 PM
Thanks for help rusbuka.

HARRY 7
05-03-2013, 07:30 PM
What could be the reason for the indoor unit to lose its code?

RusBuka
05-03-2013, 10:50 PM
Usually from electricity failures. At you it turned out to enter an option code?