View Full Version : Heatpump drier failures...



monkey spanners
21-02-2013, 09:53 PM
Anyone had any problems with two way heat pump driers failing, specificaly the check valve breaking up and blocking the drier in one direction of flow?

Any manufacturers you would recommend or avoid?

stufus
21-02-2013, 10:37 PM
Drier manufacturers or heat pump manufacturers???

If it's drier's Danfoss DMB range
If it's heatpumps depends on the application

Cheers
Stu

monkey spanners
21-02-2013, 10:53 PM
Sporlan two way driers, HH165's

The original Alco ones were ok, wish i hadn't changed them now!

stufus
21-02-2013, 11:00 PM
Sporlan are usually OK can only recall one failing and that was a long time ago.
Try to stick to Danfoss mainly as I don't have to pay the bill.
Not a fan of Alco at all could tell a few horror stories about thier stuff.
Cheers
Stu

MikeHolm
21-02-2013, 11:09 PM
You guys aren't talking domestics I expect....

monkey spanners
21-02-2013, 11:14 PM
You guys aren't talking domestics I expect....

Its on a big daikin thing, 8 cylinder comp think its about 80kw, has two driers as coil split in two circuits.

MikeHolm
21-02-2013, 11:16 PM
Thought not...

Magoo
22-02-2013, 02:19 AM
Bi-flow driers on a 80kw system seems like a cheap option, from memory the sporlans have a sprung loaded internal bypass if differential gets too high, could be totaly wrong though. I prefer Sporlan.