View Full Version : Toshiba additional refrigerant per metre? g/m



24057
21-02-2013, 07:24 PM
Hi all, need to know the recommended additional gas required per metre of piping over pre charged length. For example, Daikin say 20g/m for everything over 'x' metres. So what is Toshibas rule of thumb?

Darrenp
21-02-2013, 07:31 PM
All depends what size liquid line is , that's what daikin go on , don't know how tosh do it , possibly the same !!

Darrenp
21-02-2013, 07:33 PM
0870 843 0333 toshiba tech line , they may help

24057
21-02-2013, 07:42 PM
Liquid line is 1/4 if I remember! :)

paulg88
21-02-2013, 08:58 PM
I think 20g/metre for a 1/4 liquid line sounds right

Darrenp
21-02-2013, 09:03 PM
Prob best to bell tech , let them know the model and liquid line size and length of run they will give you correct charge

The Viking
21-02-2013, 09:50 PM
Well, this might come as a shock but...

If you click HERE (http://www.toshiba-aircon.co.uk) you will find that all the information you need about the Toshiba range is at your fingertips. All the specs, all the install and maintenance manuals, well even the O&Ms... If you get really stuck there is even a link to contact them...