16-02-2013, 09:51 AM
http://www.epeeglobal.org/epeedocs/internet/docs/EPEE_-FGas_-_position_on_the_review_-_European_Commission-_September_2012-_Final_6957.pdf
Under the existing F Gas regulation, a site would simply have to calculate what Kg refrigerant charge they have, to know what leak detection frequencies/requirements applied.
Under the new proposal, they now have to factor in the GWP and make a calculation relative to CO2 equivalent for emissions.
Leak Testing Frequencies Under new F Gas Proposal
GWP equivalent to 500 tonnes or more CO2 (Mandatory Leak check every 3 months plus MUST have fixed leak detection system
GWP equivalent to between 50-500 tonnes CO2 (Mandatory Leak check every 6 months)
GWP equivalent to between 5-50 tonnes CO2 (Mandatory Leak check every 12 months)
C
GWP
GWP equivalent to between 5-50 tonnes CO2
(Mandatory Leak check every 12 months)
GWP equivalent to between 50-500 tonnes CO2
(Mandatory Leak check every 6 months)
GWP equivalent to 500 tonnes or more CO2(Mandatory Leak check every 3 months plus
MUST have fixed leak detection system)
R404a
3,920
1.3kg
13kg
130kg
R410a
1,610
3kg
30kg
300kg
R417a
1,950
2.5kg
25kg
250kg
R422d
2,624
1.9kg
19kg
190kg
R134a
1,430
3.5kg
35kg
350kg
R407a
1,990
2.5kg
25kg
250kg
R407c
1,600
3kg
30kg
300kg
R407f
1,705
2.9kg
29kg
290kg
R507
3,298
1.5kg
15kg
150kg
The use of refrigerants such as R404a as a retrofit for R22 has always been a very poor choice and with proposed regulation changes customers will be questioning the ethics of these replacements.The GWP of R404A at 3920 is the highest of all the commonly used refrigerants.
Under the existing F Gas regulation, a site would simply have to calculate what Kg refrigerant charge they have, to know what leak detection frequencies/requirements applied.
Under the new proposal, they now have to factor in the GWP and make a calculation relative to CO2 equivalent for emissions.
Leak Testing Frequencies Under new F Gas Proposal
GWP equivalent to 500 tonnes or more CO2 (Mandatory Leak check every 3 months plus MUST have fixed leak detection system
GWP equivalent to between 50-500 tonnes CO2 (Mandatory Leak check every 6 months)
GWP equivalent to between 5-50 tonnes CO2 (Mandatory Leak check every 12 months)
C
GWP
GWP equivalent to between 5-50 tonnes CO2
(Mandatory Leak check every 12 months)
GWP equivalent to between 50-500 tonnes CO2
(Mandatory Leak check every 6 months)
GWP equivalent to 500 tonnes or more CO2(Mandatory Leak check every 3 months plus
MUST have fixed leak detection system)
R404a
3,920
1.3kg
13kg
130kg
R410a
1,610
3kg
30kg
300kg
R417a
1,950
2.5kg
25kg
250kg
R422d
2,624
1.9kg
19kg
190kg
R134a
1,430
3.5kg
35kg
350kg
R407a
1,990
2.5kg
25kg
250kg
R407c
1,600
3kg
30kg
300kg
R407f
1,705
2.9kg
29kg
290kg
R507
3,298
1.5kg
15kg
150kg
The use of refrigerants such as R404a as a retrofit for R22 has always been a very poor choice and with proposed regulation changes customers will be questioning the ethics of these replacements.The GWP of R404A at 3920 is the highest of all the commonly used refrigerants.