Kai Joon
14-02-2013, 07:22 AM
hi how's everybody , i had installed four set Daikin VRVIII RXYQ240PTJU ( RXYQ120PTJU +RXYQ120PTJU) from the master condenser ,the hot gas solenoid valve blasted with malfunction code E3 , replace with new part solenoid valve ,coil,and the filter . Three week later ,blaster again the same part with the code E4. Do someone can help me in the case coz i need to reorder the those part again to make it run in heating mode . it already wasted 85 lbs gas R410 ....i call the Daikin tech support , their said their never met this problem before ..... Thank you so much

Kai Joon
14-02-2013, 07:28 AM
blaster = pipe exploded

sendhilkmar
14-02-2013, 11:42 AM
which make solenoid valve did you use? I hope it should be compatible with R410A pressures. what was the discharge pressure you observe?

Kai Joon
14-02-2013, 02:11 PM
i'm order those part from the dealer and i'm sure that was the 100% same as the original , when high pressure ,then high pressure switch should cut off the system .... but it not ....

Kai Joon
14-02-2013, 02:15 PM
when in heating the pressure was around 145psi and 420 psi

Kai Joon
15-02-2013, 04:10 AM
1006610067

ajhvacny
11-08-2013, 02:14 PM
finally the problem is fix , that was the inverter compressor wasn't compressing so well ,sound so loud and vibration too much to cause the pipe explored . when i replace the part in second time , the error code for the inverter compressor coming out . so after replace the new compressor everything running like new before

RusBuka
11-08-2013, 05:34 PM
Since the launch of the equipment how much time passed?