View Full Version : Flooded Evaporator?



MayankBhatia
02-02-2013, 12:34 PM
Hey friends I want to know in Flooded Evaporator Why the tube Carrying water are Half filled in Shell?Upper portion of shell is empty and lower shell carrying tubes?

Rob White
02-02-2013, 03:09 PM
Hey friends I want to know in Flooded Evaporator Why the tube Carrying water are Half filled in Shell?Upper portion of shell is empty and lower shell carrying tubes?

Are you saying the shell and tube is only
half full of water?

Regards

Rob

.

Grizzly
02-02-2013, 04:41 PM
Hi Mayan.
Are you viewing this "water" (I see where you are going Rob!) through a site glass with a centrif compressor
above the evaporator?
The question is relevant, given the little amount of information you give.
Grizzly

MayankBhatia
03-02-2013, 05:41 PM
I mean The Shell Congaing Refrigerant is Half fill of tubes which contain Water.I am attaching a Similar Image.

Rob White
03-02-2013, 11:23 PM
I mean The Shell Congaing Refrigerant is Half fill of tubes which contain Water.I am attaching a Similar Image.

See

http://nptel.iitm.ac.in/courses/Webcourse-contents/IIT%20Kharagpur/Ref%20and%20Air%20Cond/pdf/R&AC%20Lecture%2023.pdf

Section 23.4.1 on page 6

There is a good explanation.

Basically it gives the refrigerant space to help liquid droplets settle.

Regards

Rob

.

Tycho
04-02-2013, 11:29 AM
See

http://nptel.iitm.ac.in/courses/Webcourse-contents/IIT%20Kharagpur/Ref%20and%20Air%20Cond/pdf/R&AC%20Lecture%2023.pdf

Section 23.4.1 on page 6

There is a good explanation.

Basically it gives the refrigerant space to help liquid droplets settle.

Regards

Rob

.

What he said :)

It's extra space to prevent liquid droplets to follow the gas stream into the compressor.

on coolers with a full set of tubes in the shell you will have an "expansion" tank on top like in this picture:
10031

MayankBhatia
04-02-2013, 07:37 PM
ThankS Rob...It helped...