PDA

View Full Version : Carrier 30RA turning stopping at night



Putte
28-01-2013, 10:31 AM
Hi!

I have a Carrier 30RA 017. It uses a Pro-dialog Plus Control and operates in local on mode. Problem is that it stops sometimes during the night or at the weekend and when i come, there are no alarms but the unit is in local off mode. I turn it on to local on and it starts and works ok. It has worked for the last 3 weeks before it stopped this time.

Alarm history shows 9, 37, 46, 36, 30. I also noticed that the alarm lights appear to be blinking in some sort of sequence even when the unit is running.

any ideas?

serviceman
28-01-2013, 05:49 PM
Could you give me the complete model of the machine? codes you mention do not appear in the manual.

Brian_UK
28-01-2013, 07:01 PM
Most of those codes seem to indicate either sensors or external switches/faults causing a shut down.

Pro-Dialog Manual...
http://eto.carrier.com/litterature/cm/13048.pdf

cool_tech
29-01-2013, 05:52 AM
Hello Brian Have the same problem with the same machine. Our machine usually stays in Remote. when the power goes out it reverts back to local off. hope it helps.