PDA

View Full Version : Daikin vrv error code 88



eurocooling
17-01-2013, 07:30 AM
Hi

Does any body know what 88 error code is on daikin vrv system need to check as the job is a five hour drive away

hyperion
17-01-2013, 08:47 AM
88 is not a normal fault code. This is the normal start up screen on the remote controller. It could be a faulty controller that is not initiating properly. Try carrying out a power reset.

AbsoluteWDJ
17-01-2013, 03:56 PM
Check wiring is connected to P1 & P2 terminals indoor unit, check wiring on back of remote control terminals

RusBuka
17-01-2013, 04:39 PM
It means you have power on remote controller, but dont have worked link board.

eurocooling
17-01-2013, 05:49 PM
Thanks for getting back owner is now saying u4 there are 11 indoor wall mounts don,t know that code

refcon32
17-01-2013, 10:46 PM
U4 error is a communication error between indoor and outdoor unit, outdoor and bs unit.
Check there is power at indoor units, outdoor, might even be a power reset outdoor and indoor units.
Thanks for getting back owner is now saying u4 there are 11 indoor wall mounts don,t know that code