PDA

View Full Version : how to evacuate a loadef reefer.



qmed
16-01-2013, 09:30 PM
I wonder if it's possible to evacuate a frozen loaded refer to change txv.

chillerman2006
16-01-2013, 10:22 PM
if its flared keep it positive and be quick

brazed , flow of nitrogen

both change drier and will be ok

R's chillerman

cadwaladr
16-01-2013, 10:26 PM
no,never enter a loaded reefer to mess with refrigerant based issues it can be fatal! get it unloaded!!!!

chillerman2006
16-01-2013, 10:30 PM
I was thinking reefer = sea going container

these have panels on the outside giving access to fans tev ect

qmed
16-01-2013, 10:45 PM
Yes, it's a seagoing container ( thermo king magnum) on a ship right now. It's braized.

qmed
16-01-2013, 10:47 PM
I don't have nitrogen either.

chillerman2006
16-01-2013, 10:52 PM
if you can access the valve

pump her down, push pull the charge out, flow of nitrogen when brazing and new drier your be ok

or in international waters with no regs

just pump her down, dont breath the phosgene when brazing, new drier and purge

learned that last one from supermarket engineers ;)

R's chillerman

qmed
16-01-2013, 10:59 PM
Thanks, guys, really appreciate it.

Magoo
17-01-2013, 01:27 AM
When you get to port get custom seals replaced by customs people on hatch covers. Saves a lot of grief, but will be a mountain of paper work

mad fridgie
17-01-2013, 02:21 AM
Un-roll it or smoke it. The most common ways to unload a reefer!

mad fridgie
17-01-2013, 02:27 AM
it is a reefer then you can pump it down, remove the refrigerant form the low side and after the reciever outlet valve. No need to decant.
As far as brazing, if you are on board , you are likely to have CO2 or Argon, either will do for a bleed, to stop oxidization. Vacuum, open up reciever valve.
No purging agent at all, braze it in, then flush through with the refrigerant, to atmosphere. )YES YES, kick my arse for purging to atmosphere.

waterskidog
20-01-2013, 05:30 AM
Truck and trailer refrigeration, get out the hoist, do a low side pump down and replace TXV. Daikin container perform an outomatic pump down and replace TXV.