View Full Version : Panasonic aquarea heat pump



fondas
05-01-2013, 07:42 AM
Hi,does anyone knows what the switch SW2 regulates at the indoor unit of an aquarea Panasonic heat pump?

install monkey
05-01-2013, 07:58 AM
doesn't mention anything in the service manual, the 4 dipswitches are in the same position on all versions so it isn't capacity

fondas
05-01-2013, 08:14 AM
i know that it doesn't mention anything in the service manual,but i'm still puzzled why is there for?
At one 16KW LTH i had an error code H12(Indoor/Outdoor capacity unmatched) every 2 days.
I've put the dipswitches 2&4 to off position and for the past 10 days the error code disappeared!!

gianfrdp
11-03-2013, 02:26 PM
12.11 Base Pan Heater Control (Optional)

To enable the base pan heater function, pin 3 of SW2 of water system PCB has to be switched from OFF to ON position.