Can somebody please advise me on the following problem.
Equipment - BOGE Refrigerant air dryer, model D670, type-429,
R134a, 17kg, LP/HP op. pr are -16/20bar.
The above dryer was tripping on LP earlier. then on doubt replaced the filter drier and cleaned the expansion valve and put back. gas charged but the problem is not solved. amount of gas charged from lp side is about 15kg (not allowing further due to the tripping on LP). we tried by heating the gas cylinder also.
observations-
when compressor is in running, HP side reading is 19bar, LP is gradually coming down to 2bar.
There is ice formation on expansion valve & up to evaporator inlet.
no icing on evaporator & temp is around 40deg.
no cooling on evaporator to accumulator piping
is there any chance of complete choking of evaporator?
there is also a bypass tubing (flo-con installed) from HP to vapor line.
Please advise what to do.
regards
tvrao
Equipment - BOGE Refrigerant air dryer, model D670, type-429,
R134a, 17kg, LP/HP op. pr are -16/20bar.
The above dryer was tripping on LP earlier. then on doubt replaced the filter drier and cleaned the expansion valve and put back. gas charged but the problem is not solved. amount of gas charged from lp side is about 15kg (not allowing further due to the tripping on LP). we tried by heating the gas cylinder also.
observations-
when compressor is in running, HP side reading is 19bar, LP is gradually coming down to 2bar.
There is ice formation on expansion valve & up to evaporator inlet.
no icing on evaporator & temp is around 40deg.
no cooling on evaporator to accumulator piping
is there any chance of complete choking of evaporator?
there is also a bypass tubing (flo-con installed) from HP to vapor line.
Please advise what to do.
regards