12-01-2006, 04:07 PM
I have a problem on a Eliwell EWPC 1000 controller the first three parameters are gone DIF LSE and HSE.Can somebody help with this problem

coolhandluke
12-01-2006, 04:52 PM
Hi Geja,

The first three parameters are factory set as follows

Dif= 2 (this is the switching differential
LSE= -55 (lowest available setpoint)
HSE= 40 (Highest available setpoint)

Try this link for a datasheet on this controller

http://www.invensyscontrolseurope.com/lwwcm/resources/file/eba6eb408fc746d/EWPC_1000_C_S_eng_1-2000.pdf

Hope this helps

Luke

tony randall
12-01-2006, 04:53 PM
what do you mean by gone?

GEJA
13-01-2006, 07:52 PM
the parameters are delete on the controler, by programming it's start on parameter 3