30-11-2012, 04:28 PM
hey guys need some help with regards to sizing hvac units,im currently in the middle east and need an estimate for the following shelter http://www.af.mil/shared/media/epubs/AFH10-222V2.pdf if you follow this link it will bring up the shelter and dimensions its page 25 of this manual for the large area maintenance shelter (lams) and it also gives you temp specifications resistant up to and down too.I would appreciate any help as to how much kw or btu of heat and cool I require for this. The climate temps where I am range from -10 to 55 derees c

Many thanks in advance Andrew

andyc425
30-11-2012, 05:39 PM
i have done a calculation and my heat loss is 285244 watts