Hi all,
Any ideas on why a wall hung split would 'spit' out water while operating? Other Mechanics have checked over and no fault found. I'm yet to check over, just getting some info prior to my visit.
Cheers

stufus
15-11-2012, 10:48 PM
Undersized,high humidity,poor airflow,blocked drain,SOG.....
Take your pick
Cheers
Stu

jimmyjewfish
16-11-2012, 04:42 AM
blocked drain, cracked drip tray,

monkey spanners
16-11-2012, 05:17 PM
Dirty coil.

install monkey
16-11-2012, 06:46 PM
drain backing up with water,may be ok most of the time but backs up after heavy use, dirty gauze on condensate pump,as others say dirty fins on coil causing water to get sucked off coil,strip unit and use nitrogen or compressed air to blast coil, be careful when using nitrogen.

regcooldude
16-11-2012, 08:08 PM
Make sure the blades on the fan impellar are not clogged with dirt. Common problem with wall mounts resulting in poor air flow.

Simeonx1
17-11-2012, 02:40 AM
low on gas causing slight icing up with a slightly dirty coil and high humidity ? does this sound likely ?

refcon32
19-11-2012, 09:50 PM
I have had this on three differant wall units during the summer this year. Evaporator coil icing up, then when unit goes off, the ice melts and pours from between wall and unit, missing the drain pan. constant icing and melting. low charge.
low on gas causing slight icing up with a slightly dirty coil and high humidity ? does this sound likely ?

mikeref
20-11-2012, 07:04 AM
Then there is the mould and scum build up behind the evaporator in tropical climates. Condensate pathways clog up and start dripping from various points.